Size of earthing cable for a drive of 700 A

Status
Not open for further replies.

maypot

Electrical
Feb 25, 2005
108
Hi,

Basically what should be the size of the earthing cable for a drive 700A capacity driving a 400 k W motor @ 400 V 50 Hz.
I am using a 300 mm^2 copper cable on the power sides.
I trust that it should be at least the size of the power cable to sustain the current under fault condition.
Furthermore, the manufacturer of the VSD is requesting an earthing cable between the VSD and the motor.

Bob
 
Replies continue below

Recommended for you

You can calculate the min cross sectional area using:

S >= (SQRT(I^2t))/k

S = Cross sectional area of earth cable
I = Fault current
t = disconnection time
k = constant determined from tables related to initial temp of conductor & type of cable

(To BS 7671)
 