CuriousElectron
Electrical
- Jun 24, 2017
- 187
Hi folks,
Should a low voltage distribution panel be sized based on total connected load plus a safety margin or based on evaluation of coincident loads ?I would think if the panel is filled out with the loads and the ratings are available, the panel bus should be sized based on 125% of maximum coincident continuous loads. Would this evaluation be considered engineering evaluation and not necessarily based on code? I know NEC has a sample guide based on residential loads, which I don't think is applicable to industrial panel sizing calculations.
Regards,
EE
Should a low voltage distribution panel be sized based on total connected load plus a safety margin or based on evaluation of coincident loads ?I would think if the panel is filled out with the loads and the ratings are available, the panel bus should be sized based on 125% of maximum coincident continuous loads. Would this evaluation be considered engineering evaluation and not necessarily based on code? I know NEC has a sample guide based on residential loads, which I don't think is applicable to industrial panel sizing calculations.
Regards,
EE