Quote: "These are circulating currents between the UPSs. They are not current being delivered to the load.
When paralleling UPSs, there are multiple inverters that are constantly adjusting their outputs to match the system output. The voltages won’t be exactly the same which induces current in the neutral conductor.
There are other scenarios that also induce current flow through the neutral. For example, if there is a load step, you may have a momentary imbalance on how the phases are loaded. In this case you would have a spike in the current through the neutral conductor."
This makes sense and also makes a point I was wondering about the design of the UPS in question... The UPS in question must be similar in design to for example, some of Alpha Technologies medium sized UPS systems in that (for purposes of discussion, assume this is a 208 3 Phase system) the UPS generates 3 phase power by the use of 120VAC modules running off a master clock with, of course, a bank of 120VAC modules generating Phase A at the 0 phase angle, the second bank of 120VAC modules timed to generate Phase B at 120 degrees and the third bank timed at the 240 degree point, for Phase C.. So you have a Y source (and from what you stated), driving a delta load.
Paralleling two UPSs of this design is no different that if the manufacturer supplied a single system with expansion cabinets for additional generating capability.. i.e. parallel rows of 120VAC modules for each of the 3 phases, all running off a common master clock and in a Y configuration.. and harmonics, imbalance loads can be flowing in the interconnecting neutral between the 2 systems up to the limits of the system, (if in worst case load). Down sizing this neutral, based on what the customer is doing today is risky, as who knows what load will be on the system tomorrow, in terms of imbalance and harmonic content. Will the manufacturer agree in writing to support the warranty on this system if not installed per their installation specs? Will AHJ approve if the installation is not in compliance with the mfg installation specifications?
While maybe not relevant to load configuration in this discussion, but given todays extensive use of switching power supplies in load equipment (e.g. server farms) and with the subsequent harmonics they generate back to the source, Alpha requires neutrals in 2 and 3 phase systems to the load to be doubled in size in relation to the phase conductors. Reason? With significant harmonic content encountered in 2 and 3 phase loads, the harmonic frequency content of current in the neutral can be in-phase, and additive, opposed to fundamental frequency current which cancels as we expect. Even if the customer load does not have this problem at installation time, the system must be installed to handle what they put on it in the future.