jerebear
Electrical
- Oct 1, 2007
- 13
We are installing 2 - 3 phase UPS modules in parallel to a common SBM. The manufacturer of the UPS is requiring a neutral being pulled in each of 4 parallel feeders from the UPS to the SBM. This neutral will not be bonded and will carry no load as all loads are 3 phase 3 wire. This neutral is only being used as a reference between the 2 UPS modules for synchronization. The manufacturer is requiring a full size neutral in each of the feeders and when asked why they stated that they only require it because they believe the code requires it. The code does allow for reducing the size of the neutral based on the unbalanced load but in reality this neutral will never carry any load. How do you go about sizing this if indeed it is to be reduced?