I need to size a TX for a piece of equipment.
1)The manufacturers spec indicates a MAX KVA of 207KVA for the machine.
2)I add up all the motors on the machine and I calc a full load KVA draw of;
152 1KW motors
2 1.4KW Air conditioners
1 5.0KW motor
1 5.5KW motor
plus some controls, electronics, displays, etc.
TOTAL CALC FULL LOAD= 165KW
3) I put a power monitor on an identical machine, only with less stations (each station has 1KW motor);
132 station reading: 75kVA, 70KW, PF:0.93
est. 152 station reading: 75KVA*(152/132)=86.6KVA
Question 1) Does anything seem unreasonable with the above information?
Question 2) Could I use a 175KVA Transformer safely? The TX is speced to handle 200% of rated load for 30sec. and 150% of rated load for 60sec. Duty cycle of one start every two hours is permitted.
*Additional info: The machine has the ability to start all stations (1KW motors) at the same time but it is not our practice to do so. We start each station one after the other.
Thanks already.
1)The manufacturers spec indicates a MAX KVA of 207KVA for the machine.
2)I add up all the motors on the machine and I calc a full load KVA draw of;
152 1KW motors
2 1.4KW Air conditioners
1 5.0KW motor
1 5.5KW motor
plus some controls, electronics, displays, etc.
TOTAL CALC FULL LOAD= 165KW
3) I put a power monitor on an identical machine, only with less stations (each station has 1KW motor);
132 station reading: 75kVA, 70KW, PF:0.93
est. 152 station reading: 75KVA*(152/132)=86.6KVA
Question 1) Does anything seem unreasonable with the above information?
Question 2) Could I use a 175KVA Transformer safely? The TX is speced to handle 200% of rated load for 30sec. and 150% of rated load for 60sec. Duty cycle of one start every two hours is permitted.
*Additional info: The machine has the ability to start all stations (1KW motors) at the same time but it is not our practice to do so. We start each station one after the other.
Thanks already.