I have a 480V switchgear with Eaton Magnum DS breakers equipped with Digitrip 1150 units.
The system ground fault is limited to 5A via a high resistance ground on the upstream transformer. As such, the Digitrip 1150 will never see the ground fault since its lowest ground fault pick-up setting is 0.25 x In.
One of the proposed solutions to detect ground fault in the 480V switchgear is to add zero-sequence CTs on each feeder, as this would help identify which feeder the ground fault exists on, and using this zero-sequence CT with the Digitrip 1150 or an external device like an I-Gard, Bender, etc.
How do I go about sizing the zero-sequence CT such that it is sensitive enough to pick up a ground fault current of <5A? Do they come in 5A:1A configurations?
The system ground fault is limited to 5A via a high resistance ground on the upstream transformer. As such, the Digitrip 1150 will never see the ground fault since its lowest ground fault pick-up setting is 0.25 x In.
One of the proposed solutions to detect ground fault in the 480V switchgear is to add zero-sequence CTs on each feeder, as this would help identify which feeder the ground fault exists on, and using this zero-sequence CT with the Digitrip 1150 or an external device like an I-Gard, Bender, etc.
How do I go about sizing the zero-sequence CT such that it is sensitive enough to pick up a ground fault current of <5A? Do they come in 5A:1A configurations?