MP Texas Engineering
Mechanical
I am trying to learn how to correctly size duct in a system. From what I understand I need to find the E.S.P. of the fan I use, and account for all pressure drops in the system, such as (coils, filters, dampers, grilles, etc.) and then use this calculation to find the design pressure loss rate(friction loss rate).
Pressure loss rate = [(External Static Pressure - Pressure Drops) * 100]/ Equivalent length of duct
Once I get this pressure loss rate I can use that to size the main duct run and critical branch. By adding dampers on the non critical branches, I can balance the other locations.
I just started working as a project engineer, and my company used the rule of thumb (.08 friction loss in w.c./100 ft) to size all duct systems before I showed up. I know this isn't necessarily acceptable, so any resources/advice is greatly appreciated.
On another note, does anyone know where to find a database with the pressure drop info for filters, coils, dampers, duct fittings, etc?