Sizing for Motor Loads Softstarter and Protective Device

Status
Not open for further replies.

garryee

Electrical
Aug 18, 2011
2
Please help me on how to size / calculate for the required rating of the softstarter and protective device for a certain motor load. Thank you in advance.
 
Replies continue below

Recommended for you

First off it probably depends on the relevant code, which you haven't stated.
 
thanks for the feedback.

i.e:

motor specs / Source:
700 HP, V = 4160, 3 phase, 60 Hz
 
No, i.e. where in the world are you? What standards and codes apply?
 
4160V 60Hz would imply the US, Canada or Mexico, maybe other South American countries like Chile that get a lot of their equipment from Canada and the US.

Assuming someone has properly sized the motor, you size the soft starter for the motor you will connect to it. I don't see the issue here. 700HP motor, 700HP starter.

Protective device? Do you mean the fuses or circuit breaker? Generally you will not have much of a choice, when you buy the soft starter, the devices inside will have been coordinated with specific fuses and you usually cannot deviate from those without violating the starter design. this is a discussion you need to have with the soft starter mfrs.