sizing of Nitrogen purge nozzle

Status
Not open for further replies.

rezapayman

Petroleum
Dec 8, 2009
19
Dear Friends
I have a pentane tank 20000 m^3 capacity and i want to know what size of nozzle can i use for Tank Nitrogen purge ?is there any refrences for it?
 
Replies continue below

Recommended for you

rezapayman,
It will depend on how quickly you want to purge, and consequently the size of your nitrogen generator. We hired a unit that could do 500 Sm3/h, but we were only purging LPG bullets of around 2000m3, and related piping. The generator had a 2" outlet, so that's the size hose we used.

Connection to the bullets for the purge was via branches in the attached piping, not via specific nozzles.

Cheers,
John
 