Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations SSS148 on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Sizing PVC pipe 5

Status
Not open for further replies.

bvelazquez

Structural
Feb 16, 2004
7
I believe this should be an easy one for you all. I am locating a PVC 4"-diameter pipe underneath a slab on grade in a loading dock area. The PVC pipe will be approximately 12 inches below the slab on grade which is approximately 6 inches thick for a total of 18 inches below the loading point. How do I determine what schedule of pipe I need in order to resist the bearing pressure from a forklift or other heavy vehicle that transmits through the concrete slab into the compacted fill and eventually over the pipe? By the time the load is transmitted to the top of the pipe, I've got about 800 psf of bearing pressure. Any sugggestions on determining schedule of pipe?
 
Replies continue below

Recommended for you

Introducing the Aquamine® system, a complete line of high impact resistant, reusable PVC pipe, fittings, valves and specialty items. Because of its superior strength and flexibility as well as other critically important features
try
 
I can’t answer your question specifically; however, if you take a look at API Recommended Practice 1102, “Steel Pipelines Crossing Railroads and Highways,” you may get some insight into the calculation method required for your problem.

At first glance, I don’t think you have a problem with the load you described. The short term uniform collapse pressure for 4” sch 40 PVC is around 100 psi. Take a look at for engineering data on PVC pipe.
 
The concrete slab distributes the forklift load. Also, if you have properly compacted fill, it bridges the pipe, taking a large proportion of the load. The load is distributed based on relative stiffness of pipe and soil. Since PVC is flexible, properly compacted soil will likely take much of the load. Is is unlikely that any special consideration of forklift load is required. However, there are standard textbook calculations that can be performed to determine the load carried by the pipe. Note that it is not the wheel load directly above it, it will be something substantially less.
 
This might help.

PWPIpe Technical Bulletin TB-D5
"Depth of Burial For PVC Pipe"

On a quick and unrepeated calc, it looks like you'll have a 0.89% (on ASTM 2729 Drain Line) deflection on the pipe (verify), which is well within the 5% recommendation.
 
jte and CRG,

This thread was a gold mine for good technical articles on PVC pipe. Your links were excellent also.

Thank you.

PUMPDESIGNER
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor