Sizing Smoke Exhaust Fan. 2

Status
Not open for further replies.

henryt1

Mechanical
Jul 18, 2011
7
First time doing the smoke exhaust. Should I base on the air change? If that is the case, how many air change should I use?
Someone, please give me your advice. Thanks in advance
 
Replies continue below

Recommended for you

what is your application and what kind of smoke did you mean?
 
Smoke control is not based in ACH, it is based on smoke volume, smoke movement, fire size, etc. Varies in different situations and application you are dealing with.

You can refer to building codes, mechanical codes, or NFPA standards.
 