2000kVA is a minimum for running it, but a quick and dirty rule of thumb is 1.5xHP to avoid a voltage drop of over 5% at start-up if you don't know anything else about the motor, starting method, load conditions, transformer and supply system. That would make it 3500kVA.
To be done correctly though, you really should do a study that includes a transient motor starting analysis. I use SKM software
Link to SKM TMS. I have also used a good one from one of our posters, Marke, which is much more reasonably priced (US$22 vs US$3,000!).
LM Photonics Electrical Calculations Software link. It compares well to the SKM unless you want to do more than just that one motor and know a lot more about the system.
There is also a freebie available from GE for use with autotransformer starters
GE Engineer's Tools link, and you can adapt it by plugging numbers. It is an Excel spreadsheet that requires you to enable macros, so do that at your own risk, but I have it and I didn't have any problems. I have compared its results against my SKM software and thought the GE freebie was a little loose however.