lancex51
Structural
- Nov 23, 2015
- 1
We do drilled piers as part of our foundations somewhat regularly. When designing, we have assumed the following IBC section to mean that 1/6th of the bearing is acceptable to use as skin friction below frost:
1810.3.3.1.4: Allowable Frictional Resistance - The assumed frictional resistance developed by any uncased cast-in-place deep foundation element shall not exceed one-sixth of the bearing value of the soil material at minimum depth as set forth in Table 1806.2, up to a maximum of 500psf, unless a greater value is allowed by the building official... etc etc about geotech reports or field testing
Assuming we say to drill and cast against earth, I feel like an assumed value of 250psf (1/6th of the 1500 minimum from IBC) skin friction is a realistic number to use. Maybe this changes depending on if they set the pour up with a sonotube instead. Thoughts?
1810.3.3.1.4: Allowable Frictional Resistance - The assumed frictional resistance developed by any uncased cast-in-place deep foundation element shall not exceed one-sixth of the bearing value of the soil material at minimum depth as set forth in Table 1806.2, up to a maximum of 500psf, unless a greater value is allowed by the building official... etc etc about geotech reports or field testing
Assuming we say to drill and cast against earth, I feel like an assumed value of 250psf (1/6th of the 1500 minimum from IBC) skin friction is a realistic number to use. Maybe this changes depending on if they set the pour up with a sonotube instead. Thoughts?