SKM Result - Negative Voltage Drop

Status
Not open for further replies.

buddy91082

Electrical
Jan 22, 2009
169
0
0
US
We are running a low voltage (<600v) drop study in SKM and are coming up with a few values with a negative voltage drop. Curious as to why the results might be coming up with a negative % voltage drop result on some of the buses and feeders and the negative % results means.

Thanks.
b
 
Replies continue below

Recommended for you

Closely bundled and long cables on lightly loaded feeders?

On long sections of transmission lines, if they are lightly loaded or open ended, the voltage swings up from the Ferranti effect.

Depending on how strong your grounding is, imbalanced load can cause overvoltages on some of your phases.
 
Power factor correction at the end of the feeders?
The cable capacitance on an unloaded or very lightly loaded cable?
Single phase loading will cause a voltage drop on the neutral which will be a voltage rise on the unloaded phases.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
All of the above responses are valid.
Are you referring to the branch voltdrop or bus volt drop ?
PTW reports bus voltdrop in percentage with respect to the nominal voltage.
eg. If the bus nominal voltage is 415V and the bus loadflow volts are 425V, then the reported LF VD% is +2.4%.
 