I have a 8 By 11 meters slab supported on beams as shown in the attached file. No meaningful continuity can be made use of along the slab edges.
Live load is 2 Kn/m2 and dead loads are 2.5 Kn/m2 with some 5kn/m lightweight partitions loads applied on the slab in the model. the slab thickness is 340 mm. Slab reinforcement for cracked analysis were 8Y16 per meter bottom reinforcement and 8Y14 per meter top reinforcement.
Your file's link is:
I have made two models in safe, with releasing the slab edges long term deflection were 30 mm. Without releasing edges, long-term deflection are 20 mm.
My question is,
1. Is using a top layer reinforcement with a development hook be enough ensure that the slab edges are fixed ?
Side note, I also used PROKON slab design module and deflections were 16 mm, even with releasing the slab edges. So I will suggest not relying on PROKON for slabs design.