As an example take a typical steel floor beam with a 38 ft. span supporting slab on composite metal deck (using 3.25 ltwt over 3 deck):
- L/240 for total load over 38ft is close to 2", at what point do you limit total to some absolute number? If you add in the girder deflection you're over 2". Assume a dropped ceiling so it's not visually an issue. At spandrels I can see an issue for facade attachments, but is there any reason to have a limit at interior beams?
- The pre-comp deflection is about 1.25". Assuming the contractor is working to a constant elevation rather than constant thickness this is an additional 12psf at midspan (probably more if accounting for the accumulated deflection of girders). How do people handle this - assume an average of say 3/4" extra concrete for ponding and carry that in the pc dead load?
Is camber worth the savings in loading from ponding concrete?
- L/240 for total load over 38ft is close to 2", at what point do you limit total to some absolute number? If you add in the girder deflection you're over 2". Assume a dropped ceiling so it's not visually an issue. At spandrels I can see an issue for facade attachments, but is there any reason to have a limit at interior beams?
- The pre-comp deflection is about 1.25". Assuming the contractor is working to a constant elevation rather than constant thickness this is an additional 12psf at midspan (probably more if accounting for the accumulated deflection of girders). How do people handle this - assume an average of say 3/4" extra concrete for ponding and carry that in the pc dead load?
Is camber worth the savings in loading from ponding concrete?