I am working on a jointless mat foundation with an exposed top face, and trying to figure out steel placement.
ACI 360-10 only makes reference to 0.5% steel "by cross-sectional area" once in a jointless slab, as far as I can tell. They don't seem to give guidance if this steel is supposed to be placed at the top only, or if it can be distributed between both faces.
ACI 224 goes on to recommend 0.6% and also doesn't seem to give guidance on placement.
This Concrete Construction mag article (Link) says to use 0.5% to 0.6% "near the top of the slab". It makes sense that it would be required at the top, where cracks propagate. My concern becomes when slabs are a bit more thick (24") for anchor rod embedment. We cant feasibly provide 0.5% in the top mat for a 24" thick slab (#7 @ 5" ??). I am debating providing 0.5% by cross sectional area, but using something like #5 @ 12" for the bottom mat, and making up the difference with bars spaced 8 - 10" OC at the top side.
Is there any published ACI language, not an article, that says where the 0.5% steel goes?