I've read through the TM5-809-12 "Concrete Floor Slabs on Grade Subjected to Heavy Loads", and found a section related to a heavy wall load on edges of the SOG. The existing slab on grade has a thickened edge, but due to the thickness of the wall being 2'~3' deep, the wall protrudes into the 5" thick SOG. I wanted to see if there is any documented calculation to check this, because I can't get this to work. The wall I'm looking at is about 2000 lb/ft.
 
Replies continue below

Recommended for you

Did you see "Table 3-3 Maximum Allowable Wall Loading Near Free Edge" in the reference you listed?
Based on that table, a 2000 lb/ft wall load on 5" thick concrete is not acceptable - as you have determined.

Wall_Load_yo7hzy.png


[idea]
[r2d2]
 
I did. I was hoping to get some explanation rather than some tabulated values or equations.
 