I have an incident of a slab-on-grade that has been placed that is exhibiting cracks in a pattern that I have not witnessed before and was hoping I could get some feedback/ideas from all here. Below is the conditions:
-6" slab on grade, 4000 mix, reinforced with WWR 6x6-W2.9xW2.9
-two "plates" were placed: #1 was 65'x520', #2 was 65'x455' (building bays are roughly 65'x65'). The plates are independent of each other, but placed within the same day. Neither are fully restrained edges. #1's long edge is against an existing building. #2's long edge is against a new foundation wall.
-only #1 plate saw the main area of cracking. The area occurred at the very beginning of the day's pour and within the first (2) bays
-the cracks exhibited "pattern" is that the cracks run parallel to only the sawcut lines running the long distance and the sawcuts are adjacent at about 1" to 12" to the sawcuts. All stay very close and parallel to the saw cuts.
-saw cuts were performed with sofcut at spacing roughly 16'3". At the area in question, the cuts were made approximately 12 hours after the concrete was placed. The cracks in question are parallel to these first (12 hr) cuts. Cuts in the perpendicular direction were cut later (13-14 hours) but did not exhibit this "parallel" pattern.
-there are other smaller/random areas, where the same parallel pattern runs the perpendicular direction, but still near/adjacent to the final saw-cut lines.
-crack width varies: hairline to 3/32"
-the cracks were not noticed when saw-cutting began. They were first noticed less than 1 day later.
-the concrete was pumped.
-minimal water was added.
-slumps averaged 6.5" and were consistant.
-breaks came back good - all passing and none WAY over.
-no super admixtures added.
-"story" from the site was when the day's pour began, the beginning (where these cracks are found) of it saw a lot of "commotion" e.g. the crew trying to rush and keep up with the trucks pumping the concrete in. Later, the timing of unloaded concrete with the crew placing it feel into a better timing/rhythm.
The field superintendent has provided us a drawing showing all of the cracks. Its uncanny how close these cracks marry up and hug next to the final saw cuts. Some designers may say this proves that the saw-cut pattern we prescribed is correct since its supposed to "mimic" where the slab would naturally crack. Thats good in theory, but isn't a hard science. These cracks are almost dead-on (relatively speaking). I can't figure the reason why, but my gut tells me the saw-cutting caused it.
There may be more info I can provide to help enlighten this case, just ask.
I appreciate any feedback.
Thanks
-6" slab on grade, 4000 mix, reinforced with WWR 6x6-W2.9xW2.9
-two "plates" were placed: #1 was 65'x520', #2 was 65'x455' (building bays are roughly 65'x65'). The plates are independent of each other, but placed within the same day. Neither are fully restrained edges. #1's long edge is against an existing building. #2's long edge is against a new foundation wall.
-only #1 plate saw the main area of cracking. The area occurred at the very beginning of the day's pour and within the first (2) bays
-the cracks exhibited "pattern" is that the cracks run parallel to only the sawcut lines running the long distance and the sawcuts are adjacent at about 1" to 12" to the sawcuts. All stay very close and parallel to the saw cuts.
-saw cuts were performed with sofcut at spacing roughly 16'3". At the area in question, the cuts were made approximately 12 hours after the concrete was placed. The cracks in question are parallel to these first (12 hr) cuts. Cuts in the perpendicular direction were cut later (13-14 hours) but did not exhibit this "parallel" pattern.
-there are other smaller/random areas, where the same parallel pattern runs the perpendicular direction, but still near/adjacent to the final saw-cut lines.
-crack width varies: hairline to 3/32"
-the cracks were not noticed when saw-cutting began. They were first noticed less than 1 day later.
-the concrete was pumped.
-minimal water was added.
-slumps averaged 6.5" and were consistant.
-breaks came back good - all passing and none WAY over.
-no super admixtures added.
-"story" from the site was when the day's pour began, the beginning (where these cracks are found) of it saw a lot of "commotion" e.g. the crew trying to rush and keep up with the trucks pumping the concrete in. Later, the timing of unloaded concrete with the crew placing it feel into a better timing/rhythm.
The field superintendent has provided us a drawing showing all of the cracks. Its uncanny how close these cracks marry up and hug next to the final saw cuts. Some designers may say this proves that the saw-cut pattern we prescribed is correct since its supposed to "mimic" where the slab would naturally crack. Thats good in theory, but isn't a hard science. These cracks are almost dead-on (relatively speaking). I can't figure the reason why, but my gut tells me the saw-cutting caused it.
There may be more info I can provide to help enlighten this case, just ask.
I appreciate any feedback.
Thanks