Skay999
Structural
- Dec 7, 2022
- 7
Currently looking at designing a slab on grade for a small transformer (40 kips). The slab is currently 18 inches thick (controlled by frost depth) and I am trying to figure out the reinforcement design.
I looked into ACI 360R and they require a minimum of 0.5% to eliminate the need for sawcut joints. However, if my slab's longest dimension is less than the required joint spacing (8ft by 14ft slab), would I need to follow this 0.5% rule to limit crack widths? In this case, would the minimum temperature and shrinkage reinforcement refer back to ACI 318 (the 0.0018Ag)?
Also, if I have an overturning moment on the transformer due to wind/seismic, should the slab be designed for this concentrated moment? Would I just go back to ACI 318 to determine the flexural reinforcement needed?
Thinking of going with #6's at 12 inches c/c both ways, top and bottom.
I looked into ACI 360R and they require a minimum of 0.5% to eliminate the need for sawcut joints. However, if my slab's longest dimension is less than the required joint spacing (8ft by 14ft slab), would I need to follow this 0.5% rule to limit crack widths? In this case, would the minimum temperature and shrinkage reinforcement refer back to ACI 318 (the 0.0018Ag)?
Also, if I have an overturning moment on the transformer due to wind/seismic, should the slab be designed for this concentrated moment? Would I just go back to ACI 318 to determine the flexural reinforcement needed?
Thinking of going with #6's at 12 inches c/c both ways, top and bottom.