Hi All,
would it be sufficient to use below calculations for a slab supported on grade? I am working to book (Reinforced Concrete Design to Eurocodes Design Theory and Examples Fourth Edition)
simply supported two-way slab: Corners free to lift
* Design of moment reinforcement
* Shear resistance
* Deflection


 
Replies continue below

Recommended for you

As he asked, if it is supported on grade, what is the span? The method you are suggesting has edge support, not on grade support.
 
Hi I have attached what i have calculated for the slab.
The slab is 6.19 x 3.031 x 0.150 meters and yes i no what i have calculated is not for a slab on grade, I was just trying to ascertain if the simply supported two way slab calculations attached could be used as an over estimate or substitute to using TR34 calculations.

 
 https://files.engineering.com/getfile.aspx?folder=c67ee8cf-04d9-4b48-87fa-f53d47bca538&file=simply_supported_two-way_slab.pdf
Using the proposed two way slab formula, only bottom reinforcement would be required. Top reinforcement would be required if the slab is on a swelling soil or if the edges are sustaining line loads which must be resisted by the slab.

BA
 
Status