Hello. I am trying to limit the PID controller output to a certain percentage. I set the percentage, and selected "YES" to enable output limiting, but the PLC always defaults back to "NO" after the machinery has been shut down for the night. How do I make the limit stay in place? Thanks in advance. Jerry
 
Replies continue below

Recommended for you

best guess is that that when the PID qualifies in the program is where you need to put a move statement in to overwrite that parameter to the YES state. If it is a YES then its maybe a booleen, so a "YES" latch bit would be the second guess.

I did not consult the manual for PID, so maybe you should do this for the correct parameter for the percentage.
 