Dear Colleagues,

The AISC code limits the slenderness for both compression and tension members.
Which value we should consider for buckling factor K of lambda=k*l/r for calculate the slenderness ratio of a tension member, taking account that the values of K was stablished for members under compression load under some combinations of external supports? Should we use 0.5 teorical(0.65 Recommended for fixed-fixed ends) for all cases?

Thanks,

Marx Pio
 
Replies continue below

Recommended for you

The effective length factor, K, does not apply to the slenderness ratio recommendation for tension members. See AISC specification section B7. In other words, use K=1 for all cases in tension.
 
Yes,

And additionally: AISC does not mandate the limit on the slenderness ratio, but rather recommends a limit. They use the word "preferably".
 
Agree in determining the slenderness on actual length for members in tension, or take K=1.

... and the preferably is preferable, will the member some day enter in -even marginal- compression?. I think they degraded it to preferably because otherwise the cable or tensors practice would become too much in evidence.
 