cme

Mechanical
Jan 16, 2003
196
I got a problem with very little ceiling space for a 4-pipe fan coil units to serve a corridior.

7" total ceiling space for ceiling mounted units .... similar to EMI CAF4-08 ....... EMI's are 9+"

Will take a wall mounted (up high) near the ceiling ..... something slimline w/ integral condensate pump.

I don't have room for an air system.

Thanks
 
Replies continue below

Recommended for you

I have no room for ductwork
 
Consider console type unit located in room of consider horizontal unit installed in toilet room that can have lower ceiling & fan coil discharged ti adjacent corridor.
 
This is an old hospital circa 1915 ..... corridor is non-patient ....... there is a slew of electrical conduits/steam/pumped condensate lines above the ceiling.

The ceiling height is 7'-0".

The walls are 12" thick concrete.

They don't build them like this today.
 
Try a company called Multi-Aqua. I Believe they have some wall mounted units.
 