Hello,
Table J3.1 in AISC 13th Edition gives the minimum bolt pretension values (148 kips for a 1.5 inch A490 bolt). I have to design a slip-critical connection using equation J3-4. Can I use a higher value for bolt pretension (160 kips) in this equation? Does AISC specify the maximum bolt pretension value for bolts?
I am using a slotted hole (hole length= 2.625 inch). As per AISC the hole factor for a short slotted hole (hole length is 1.875 inch for 1.5 inch bolt) is 0.85 and for a long slotted hole (hole length is 3.750 inch for 1.5 inch bolt) is 0.70. Can I use the linearly interpolated hole factor of 0.79 for hole length of 2.625 inch?
Regards,
Su
Table J3.1 in AISC 13th Edition gives the minimum bolt pretension values (148 kips for a 1.5 inch A490 bolt). I have to design a slip-critical connection using equation J3-4. Can I use a higher value for bolt pretension (160 kips) in this equation? Does AISC specify the maximum bolt pretension value for bolts?
I am using a slotted hole (hole length= 2.625 inch). As per AISC the hole factor for a short slotted hole (hole length is 1.875 inch for 1.5 inch bolt) is 0.85 and for a long slotted hole (hole length is 3.750 inch for 1.5 inch bolt) is 0.70. Can I use the linearly interpolated hole factor of 0.79 for hole length of 2.625 inch?