JAE
Structural
- Jun 27, 2000
- 15,463
I've got a large wood framed (one story) building that is framed with load-bearing wood stud walls and shearwalls that support combinations of wood trusses (pre-engineered) and steel beams.
In most cases, the steel wide flange beams support the wood trusses.
At issue is what to do with a multitude of interior non-load bearing wood stud walls that want to frame up to the bottom of the wood trusses. We are trying to establish our design criteria for the steel beams where we want to keep the vertical deflection under control.
We are using L/360 for the roof snow load as one limit to never exceed.
We also are using 1/2" as an absolute limit for steel beam deflection to ensure that we don't damage partitions below. This is resulting in some very large beams controlled by this deflection.
But we are thinking that maybe we could go higher than 1/2" if we provide some kind of slip connection at the juncture of the partition to the bottom of the truss. Metal studs have those slip tracks that can be used...but in wood - are there any details out there that address this. The partitions sit on the concrete slab below so there is no give should the truss try to bear on the partition.
In most cases, the steel wide flange beams support the wood trusses.
At issue is what to do with a multitude of interior non-load bearing wood stud walls that want to frame up to the bottom of the wood trusses. We are trying to establish our design criteria for the steel beams where we want to keep the vertical deflection under control.
We are using L/360 for the roof snow load as one limit to never exceed.
We also are using 1/2" as an absolute limit for steel beam deflection to ensure that we don't damage partitions below. This is resulting in some very large beams controlled by this deflection.
But we are thinking that maybe we could go higher than 1/2" if we provide some kind of slip connection at the juncture of the partition to the bottom of the truss. Metal studs have those slip tracks that can be used...but in wood - are there any details out there that address this. The partitions sit on the concrete slab below so there is no give should the truss try to bear on the partition.