Smoke Detector on 100% Make-up Air Systems?

Status
Not open for further replies.

MGMM

Mechanical
Joined
Nov 4, 2003
Messages
6
Location
US
Are duct (smoke) detectors or building fire alarm interlock (for disabling the unit)required on 100% make-up air systems with 2000 or more CFM?

I have a commercial kitchen in our nursing home that has a 100% 3600 CFM make-up air unit as relief for our grease hood. Our suppression alarm company responsible for the hood ansul system says that the NFPA 90 only requires that the hood exhaust fan be interlocked with an over-ride such that when the ansul system is tripped the exhaust fan is kept on to remove smoke and heat, and that no interlock or lock-out from the ansul control to the make-up air unit is required.

Please advise.

GMG

 
I did an acceptance test for a retail store with 4 individual roof top HVAC units. Each of the units functioned independently when we smoke tested them. I would imagine that the same would be with your situation. The two units would be independent.
 