Smoke exhaust at Mall with 15 m height (NFPA and ASHRAE)

Status
Not open for further replies.

Vusal Quliyev

Mechanical
Dec 4, 2018
26
Dear FF experts,

I am searching standard for Smoke Exhaust at Mall with just 15 m height. There are just 3 levels in the project. Is NFPA or ASHRAE states that Smoke exhaust is necessary at corridors? Please help.


Thanks.
 
Replies continue below

Recommended for you

You might want to check NFPA 92. There are also some ASHRAE publications on the subject which you can find in their website.
 
Dear UFT12,
I could not fined any information about smoke required or not at mall with 15 m height and 3 levels.

:(
 
If you re looking for a requirement about smoke control/exhaust you should look in your applicable building code or contact your AHJ. NFPA 92 is a design standard. You will not find this requirement there.
 