Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Smoke exhaust at Mall with 15 m height (NFPA and ASHRAE)

Status
Not open for further replies.

Vusal Quliyev

Mechanical
Joined
Dec 4, 2018
Messages
26
Location
AZ
Dear FF experts,

I am searching standard for Smoke Exhaust at Mall with just 15 m height. There are just 3 levels in the project. Is NFPA or ASHRAE states that Smoke exhaust is necessary at corridors? Please help.


Thanks.
 
You might want to check NFPA 92. There are also some ASHRAE publications on the subject which you can find in their website.
 
Dear UFT12,
I could not fined any information about smoke required or not at mall with 15 m height and 3 levels.

:(
 
If you re looking for a requirement about smoke control/exhaust you should look in your applicable building code or contact your AHJ. NFPA 92 is a design standard. You will not find this requirement there.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top