JohnnnyBoy

Structural
Oct 13, 2015
81
All,

I've recently read this thread about snow loading and grating and there does seem to be a mixed opinion on it.

I'm currently desiging a frame system to support a MUA unit for a soccer field. The platform is to be 16'-6" x 27'6" x 8'-0" high and placed against a much higher structure. Through some very quick snow drift calculations the inside edge would accumulate a snow load of approximately 80psf and the outside edge to be quick significant as well as it would drift against the MUA unit.

My question is weather I should account for this or not or have a reduction factor at least for the snow load.

My factored weight of the unit is 55psf assuming 10psf dead load for the structure.
Now I'm questioning for my live/snow load if I should calculate 1.5 * 20 psf Live + 0.5 * Snow Drift Loading or can eliminate altogether.

Any opinions would help.
 
Replies continue below

Recommended for you

Assuming there is a certain amount of bridging that would occur on the grating i've never personally seen grating with the amound of snow of a normal structure/support system. Also It seems like quite the over design if I were to design for full drift loading, 0.5 Live loading and Dead loading.
 
Where are you, and do you ever get ice storms with snow over the ice?

Is there any heat coming up from the grated area, like a transformer vault?




Mike McCann, PE, SE (WA)


 
In Alberta so yes we do get ice storms with the possibility of the grating freezing over but again I have not seen it practice that much. In saying this although I don't see it in practice although this does not mean it shouldn't be design for.

The only heat that may occur is heat loss from the Make Up Air Unit.
 
You don't consider snow and live load on roofs. I don't see how this is any different. Your load cases 1.25D + 1.5L or 1.25D + 1.5S + 0.5(live load on platforms without snow). In my mind there is enough bridging it sees full snow load though, I have some grating at my place and snow piles on it sometimes. Of course if you shovel it or something it falls right through.
 
Okay thanks, that's what Ill go with. I wasn't sure if a platform would be considered the same as a roof. But your right if a worker was to be working up there during winter, it would be shoveled before he works therefore should not consider both.

Thanks for the Help!
 
Well, the worker shoveling is certainly a live load = his own weight, plus the snow and ice weight (maximum thickness) + the dynamic lifting and throwing forces of each shovel/snowblower action. Fingles Law says the snow and ice will occur at the worst possible combination too of loading: equipment and lights and "temporary cables" for example, left up on the scaffolding before the storm.

But maximum wind will probably not occur at the same time as shoveling.
 
For what it's worth, I've definitely seen grating (bar spacing typically 1.25" O/C) accumulate a lot of snow, even to the point of drifting several feet deep. If the weather is right (wrong?), it is a possibilty that you could accumulate a bunch.
 
According to "Snow Loads on Non-Building Structures" (the authors state in reference to snow on grating that "balanced snow will accumulate on this surface just as it would on a checkered plate or any other continuous flooring material". They further state that snow drift should be considered.

I've also seen snow accumulate on grating as if it were a solid surface.
 