Jed057

Electrical
Mar 18, 2009
35
0
0

If we need to start for so-lo run Compressor 2600 kW ,11 kV.
How big diesel generator, we need to prepare for testing.

Thanks
 
Replies continue below

Recommended for you

Safe choice: 7800 kW
Starting the compressor only with no other loads: Possibly 6500 kW
A smaller generator may be possible in the case of special circumstances or combined generator/compressor starting.
For VFD starting use 5200 kW. Minimum 200%, to allow for distortion wave form and its effect on the Automatic Voltage Regulator. (AVR)

Bill
--------------------
"Why not the best?"
Jimmy Carter
 