Soft Start considered power conversion equipment?

Status
Not open for further replies.

buzzp

Electrical
Nov 21, 2001
2,032
Is a soft start considered power conversion equipment by the NEC? I am referring to NEC2011 430.122(B). This section talks about bypass devices. I think the answer is no but would like confirmation. The section says conductors feeding these devices with a bypass needs to be sized on 125% of the input to the conversion equipment or 125% of the motor FLC. This is not a big deal one way or the other for my application but would like to know for future. Thanks!
 
Replies continue below

Recommended for you

Echo.
A soft starter is no different (in the eyes of the NEC) from any other motor starter.


"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
 