soft start specifying

Status
Not open for further replies.

ILCML

Electrical
Jan 4, 2007
52
I have seen in here before "rules" of specifying a soft starter concerning voltage rating relationship between motor and starter, and now cannot find it.

I need to specify a soft starter and cannot remember if it needed to be rated higher than the motor or the same voltage...am I thinking of VFD's?
 
Replies continue below

Recommended for you

Both just need to be rated for the given source and motor voltages. Nothing extra.

Now current or 'capacity' wise it some times makes a difference.

Generally if you have starting loads that are rough you might need a "heavier duty" softstarter.

Keith Cress