Reviewing a design for a solar PV park with inverter step up transformer (to 22 kV) connected in Dyn11, with the delta facing 22 kV and wye facing 600 V (inverter side).
Array power is evacuated to a 22 kV switchgear through radial feeder with ring main units.
The receiving substation (some 2-3 km away) has a step-up 22/220 kV ddYN three winding transformer and grounding (zig-zag) transformer is used to detect SLG faults. feeders are arranged on normally opened bus sections on 22 kV side.
I wonder why inverter step up transformer is connected in Dyn11 with wye facing power flow direction rather than YNd11? Note that with YNd11 connection, the additional zig-zag transformer will not be needed.
Any clues?