Coco_HueHueHue
Electrical
- Apr 8, 2018
- 49
Hello,
Quick question that keeps me a bit confused since i almost never worked with enclosed trays.
Canadian Electrical Code asks me to interpret enclosed cable trays (solid bottom with solid cover) a bit as a single big raceway.
So, i need to add the number of conductors to apply the appropriate de-rating in ampacity to the cables.
I was thinking to install a divider to separate controls cables from power cables. But, having the control cables in the same tray as the power cables (remember, i need to interpret both in the same tray as enclosed tray even if i have a spacing since the code interprets an enclosed tray as one big raceway) brings the total number of conductors very high while i only have 6 power conductors.
In a ventilated tray, with a diameter spacing between control cables and power cables, i would have a de-rating factor of 0,8 only for 6 conductors.
But, adding up those control cables, the number of conductors indicate a de-rating factor of 0,5 (43+ conductors).
However, those control cables do not generate heat (or very little... neglectable...).
I would like your opinion on that... can i not consider the control cables in the total number of conductors and only consider power cables?
Thank you for your input.
Quick question that keeps me a bit confused since i almost never worked with enclosed trays.
Canadian Electrical Code asks me to interpret enclosed cable trays (solid bottom with solid cover) a bit as a single big raceway.
So, i need to add the number of conductors to apply the appropriate de-rating in ampacity to the cables.
I was thinking to install a divider to separate controls cables from power cables. But, having the control cables in the same tray as the power cables (remember, i need to interpret both in the same tray as enclosed tray even if i have a spacing since the code interprets an enclosed tray as one big raceway) brings the total number of conductors very high while i only have 6 power conductors.
In a ventilated tray, with a diameter spacing between control cables and power cables, i would have a de-rating factor of 0,8 only for 6 conductors.
But, adding up those control cables, the number of conductors indicate a de-rating factor of 0,5 (43+ conductors).
However, those control cables do not generate heat (or very little... neglectable...).
I would like your opinion on that... can i not consider the control cables in the total number of conductors and only consider power cables?
Thank you for your input.