tstructural
Structural
- Nov 3, 2014
- 43
I'm a structural engineer but am currently working with a manufacturing facility that produces commercial Air Handling Units. They've asked me to update their Structural Design Checklist for HVAC units in USA. I've come across some information that seems incorrect but don't want to delete it just in case I'm wrong.
FYI - We have pre-approved OSHPD units for high seismic but also sell units in low seismic areas. We provide units for the health care industry as well as others. We also sell to the VA sometimes.
The following are the items that I believe to be incorrect. If I'm wrong - please let me know and also tell me which code I should have so I can see the requirements:
1. if the occupancy importance factor (Ip) is 1.0 and the Seismic Design Category is A, B or C then no IBC certification is required.
2. analytical calculations are acceptable (meaning no testing - just hand or computer calculations) if the Ip = 1.0 and the Seismic Design Category is D, E or F.
3. analytical calculations are NOT acceptable (meaning we would have to test the units on a shake table) if the Ip=1.5 and the Seismic Design Category is C,D,E or F.
For item #1 above - wouldn't our products always have to meet IBC requirements regardless of it being in a low seismic region?
Item #2 and #3 together imply that High Importance (health care and high tech) always require shake table tested units if located in medium to high seismic regions. I've never heard of hand or computer generated calculations NOT being good enough for an IBC certified design
FYI - We have pre-approved OSHPD units for high seismic but also sell units in low seismic areas. We provide units for the health care industry as well as others. We also sell to the VA sometimes.
The following are the items that I believe to be incorrect. If I'm wrong - please let me know and also tell me which code I should have so I can see the requirements:
1. if the occupancy importance factor (Ip) is 1.0 and the Seismic Design Category is A, B or C then no IBC certification is required.
2. analytical calculations are acceptable (meaning no testing - just hand or computer calculations) if the Ip = 1.0 and the Seismic Design Category is D, E or F.
3. analytical calculations are NOT acceptable (meaning we would have to test the units on a shake table) if the Ip=1.5 and the Seismic Design Category is C,D,E or F.
For item #1 above - wouldn't our products always have to meet IBC requirements regardless of it being in a low seismic region?
Item #2 and #3 together imply that High Importance (health care and high tech) always require shake table tested units if located in medium to high seismic regions. I've never heard of hand or computer generated calculations NOT being good enough for an IBC certified design