I have designed sonotube piers for many years for light use residential decks basically, where
the reaction is around 2500 lbs, the sono tube is 10 inch diameter and extends 3 to 4 foot into the ground
where it is supported by a pad footing. We never used ties. The guy who taught me never used ties.
ACI requires that concrete piers have minimum longitudinal and tie reinforcement (.0025 % for vertical steel)
I have seen requiremenst for 4 bars min, and ties at a spacing of 16 bar diameters.
I seldom see engineers or builders put ties in these type of concrete supports.
I know that code says do it.....is there somewhere in the code that gives an exception? I can't seem to find it.
It seems like overkill; I know I know....follow the code. I'm just trying to see if practicality has caught up to the code creators.