Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

Spacing of electrical equipment in a substation

Status
Not open for further replies.

dup18

Electrical
Feb 27, 2012
18
0
0
US
All,
I am probably missing the obvious, but what document(s) are used to determine the horizontal clearances (spacing) between various pieces of electrical equipment (disconnect switch, circuit breaker, circuit switcher, metering PT/CT, etc. in a 115 kV substation?

Podo
 
Replies continue below

Recommended for you

I would imagine that limits of approach. Distance between phases and the location of each piece of equipment would dictate your site's footprint.
 
Thanks for the responses. I could not figure out that the bases (and the first 8 feet high) are basically grounded metal. Breaker control cabinets may contain 120 AC or DC. Yet the equipment is spaced far apart. Room for a truck to travel, and I guess room to remove/install some of the larger equipment - true, but more dictated by maintenance than safety codes.

Take care and thanks again.
Podo
 
Status
Not open for further replies.
Back
Top