spacing to ground at 5kV 1

Status
Not open for further replies.

standaman

Geotechnical
Oct 26, 2006
1
What is the spacing in inches from a 5kV cable lug to ground, in this case the cover of a j-box?
standaman
 
Replies continue below

Recommended for you

depends where you are and what type of system you have...

CSA 4160V is 2.5" P-G and 3.25" P-P...

However if your system is resistance grounded instead of solidily you should use the 3.25" for both P-P and P-G..

Any case if you can get P-P go for it..

Regards,
TULUM



 
And these are **minimums**. More is better.
 