Good day all,
My aim is to block the Incomer's over current and earth fault setting once the Feeder relay picks up a fault.
Using the SPAJ 141C module SPCJ 4D24. The Feeder relay (SPAJ 141C) sends out a Start Signal to the incomer (once a fault is picked up) on terminal 74 & 75 (Start 1) with SGR3/1,3,5, and 7 switched on (1).
The Start signal Start 1 is connected to the Incomer, terminal 11&12 (External Control). The settings in SGB1/1,2,3 and 4 is switched on (1) to block the over current and earth fault pickup on the incomer.
Once the Feeder clears the fault and the start signal falls away, the incomer then has no blocking signal on the External Control.
I simulated the test using an Omicron CMC 356, with current channel A on the Feeder and current channel B on the Incomer. Using the State sequencer module I injected both currents so that the relay picks up a fault and sends out a start signal to the Incomer, but the problem is that the Incomer does nothing with the External control signal. Hopefully I'm missing something small.
Thanks for helping.
My aim is to block the Incomer's over current and earth fault setting once the Feeder relay picks up a fault.
Using the SPAJ 141C module SPCJ 4D24. The Feeder relay (SPAJ 141C) sends out a Start Signal to the incomer (once a fault is picked up) on terminal 74 & 75 (Start 1) with SGR3/1,3,5, and 7 switched on (1).
The Start signal Start 1 is connected to the Incomer, terminal 11&12 (External Control). The settings in SGB1/1,2,3 and 4 is switched on (1) to block the over current and earth fault pickup on the incomer.
Once the Feeder clears the fault and the start signal falls away, the incomer then has no blocking signal on the External Control.
I simulated the test using an Omicron CMC 356, with current channel A on the Feeder and current channel B on the Incomer. Using the State sequencer module I injected both currents so that the relay picks up a fault and sends out a start signal to the Incomer, but the problem is that the Incomer does nothing with the External control signal. Hopefully I'm missing something small.
Thanks for helping.