NEMA MG-1 states the following:
14.31 MACHINES OPERATING ON AN UNGROUNDED SYSTEM
Alternating-current machines are intended for continuous operation with the neutral at or near ground
potential. Operation on ungrounded systems with one line at ground potential should be done only for
infrequent periods of short duration, for example as required for normal fault clearance. If it is intended to
operate the machine continuously or for prolonged periods in such conditions, a special machine with a
level of insulation suitable for such operation is required. The motor manufacturer should be consulted
before selecting a motor for such an application.
Grounding of the interconnection of the machine neutral points should not be undertaken without
consulting the System Designer because of the danger of zero-sequence components of currents of all
frequencies under some operating conditions and the possible mechanical damage to the winding under
line-to-neutral fault conditions.
Other auxiliary equipment connected to the motor such as, but not limited to, surge capacitors, power
factor correction capacitors, or lightning arresters, may not be suitable for use on an ungrounded system
and should be evaluated independently.
Please consider each of the following questions individually:1 - Would/should a motor supplier give you any different insulation if you tell him the motor operates on 480vac ungrounded system than if you tell him the motor operates on 480vac grounded system? Would the answer to this question have been any different in early 1980's?
2 - Shouldn't a standard 480vac motor should be adequate even for mild transient overvoltages expected in ungrounded system. Factory hi-pot is 2kv which is around 7 times normal line to ground (~260vac). Maintenance hi-pot levels are in the range of 1.5kvdc.
3 - If standard 480v motor is adequate/reliable and is all that an OEM would provide for this specificaiton, then what is the purpose of the NEMA statement quoted above. Perhaps it is intended towards higher voltage systems where the margin between hi-pot voltage and normal line-to ground becomes much smaller (using the 2*kv+1 rule the 1 plays huge role for 480v motor but diminishing role for higher voltage motors).
14.31 MACHINES OPERATING ON AN UNGROUNDED SYSTEM
Alternating-current machines are intended for continuous operation with the neutral at or near ground
potential. Operation on ungrounded systems with one line at ground potential should be done only for
infrequent periods of short duration, for example as required for normal fault clearance. If it is intended to
operate the machine continuously or for prolonged periods in such conditions, a special machine with a
level of insulation suitable for such operation is required. The motor manufacturer should be consulted
before selecting a motor for such an application.
Grounding of the interconnection of the machine neutral points should not be undertaken without
consulting the System Designer because of the danger of zero-sequence components of currents of all
frequencies under some operating conditions and the possible mechanical damage to the winding under
line-to-neutral fault conditions.
Other auxiliary equipment connected to the motor such as, but not limited to, surge capacitors, power
factor correction capacitors, or lightning arresters, may not be suitable for use on an ungrounded system
and should be evaluated independently.
Please consider each of the following questions individually:1 - Would/should a motor supplier give you any different insulation if you tell him the motor operates on 480vac ungrounded system than if you tell him the motor operates on 480vac grounded system? Would the answer to this question have been any different in early 1980's?
2 - Shouldn't a standard 480vac motor should be adequate even for mild transient overvoltages expected in ungrounded system. Factory hi-pot is 2kv which is around 7 times normal line to ground (~260vac). Maintenance hi-pot levels are in the range of 1.5kvdc.
3 - If standard 480v motor is adequate/reliable and is all that an OEM would provide for this specificaiton, then what is the purpose of the NEMA statement quoted above. Perhaps it is intended towards higher voltage systems where the margin between hi-pot voltage and normal line-to ground becomes much smaller (using the 2*kv+1 rule the 1 plays huge role for 480v motor but diminishing role for higher voltage motors).