sedesigner06

Structural
Jan 10, 2014
58
I am working incorporating the design and detailing requirements of a Special Reinforced Masonry Shear Wall (R=5) for a seismic design category D structure. My only option is to use a SRMSW and cannot use intermediate to relieve the detailing requirements.

I am reading ACI 530-13 7.3.2.6 d stating:

"Shear Reinforcement shall be anchored around vertical reinforcing bars with standard hook" with the commentary noting "This requirement is intended to avoid a splice failure in such reinforcement.

My Questions are:

1) Does anyone have a detail showing this, I have looked at a lot of standard masonry details and never ran across one showing a hook around vertical reinforcing.

2) My interpretation of the commentary is I cannot use development length in any scenario...hooked on both ends and then placed over vertical reinforcing within a bond beam? Seems odd and crowed

I typically use (2) #5 in bond beams at 4'-0'' OC, seems if my interpretation is correct it my be better to use #4's for tighter hooks and less crowding and choke down the spacing if needed to make sure the proper reinforcement ratios are met.

Thanks in advance for any help.
 
Replies continue below

Recommended for you

I don’t usually show a detail. I just have a general note that says the bars need to have a stabdard hook. I verify that when I review the shop drawings. If you want a detail you would just show a hook around the vertical corner bars. Regarding the bar size it depends on what size cmu block you have. An 8” block might be tight with (2) #5’s but not impossible. I’ve seen guys angle the hooks so they fit. It does get crowded at the corners which is why having a quality Contractor is key to making sure the grout is properly placed.
 