Here is an opinion on how to specify the max pressure and temperature for process measurement instrumentation.
In order to prevent the pressure/temperature rating of the instrumentation becoming a weak point of the system, for the max pressure or temperature specified on the datasheet, process upset scenarios (except fire) should be take into account in additional to the normal operating range. The suggestion was that,
1.For process measurement instrumentation on vessels, the max P/T data should be specified as being consistent with the vessel rating, i.e. to use the vessel design pressure or PSV set pressure whichever lower as the max pressure, and vessel design temperature as the max temperature for the instrumentation;
2. For process measurement instrumentation on piping, the max P/T data should be specified as consistent with the piping specification. such as ANSI 600# class with correspondence temperature range.
I agree this will ensure the inherent safety design/selection of the instrumentation. My concern is, the design/selection of transmitters usually gives 1.5 times of safety factor for over range protection. If the max P/T data is specified as the same as vessel or piping rating, could that result in over-rated instrumentation or increased project cost?
How would do you specify the max pressure and temperature for process measurement instrumentation?
In order to prevent the pressure/temperature rating of the instrumentation becoming a weak point of the system, for the max pressure or temperature specified on the datasheet, process upset scenarios (except fire) should be take into account in additional to the normal operating range. The suggestion was that,
1.For process measurement instrumentation on vessels, the max P/T data should be specified as being consistent with the vessel rating, i.e. to use the vessel design pressure or PSV set pressure whichever lower as the max pressure, and vessel design temperature as the max temperature for the instrumentation;
2. For process measurement instrumentation on piping, the max P/T data should be specified as consistent with the piping specification. such as ANSI 600# class with correspondence temperature range.
I agree this will ensure the inherent safety design/selection of the instrumentation. My concern is, the design/selection of transmitters usually gives 1.5 times of safety factor for over range protection. If the max P/T data is specified as the same as vessel or piping rating, could that result in over-rated instrumentation or increased project cost?
How would do you specify the max pressure and temperature for process measurement instrumentation?