Why does some motor manufacturers specify (on their nameplate data) using a 370 volt capacitor on their 460 volt single phase motors?
 
Replies continue below

Recommended for you

Maybe because the capacitor is not exposed to the full line voltage. Try to find a vector diagramm showing voltages for a single phase induction motor with auxiliary winding.
 
The starting winding may be a 240 volt winding. If so, it would be fed from one line and the center connection between the 240V/480V run winding.
It is common for 115V/230V motors to have a single 115V starting winding.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 