Hello Everybody,
I have a case where a valve is needed for regulating the pressure inside a process. The issue is that the pressure setpoint(and flow required to maintain this pressure) varies quite a lot. The valve(s) is installed downstream of the process, and the process itself has inlet flow controlled.
The minimum flow is on the order of 10% of design flow, max flow 120% of design. Pressure setpoint can vary anywhere between 3 barg to 8 barg (but not likely high pressure at low flows).
So far my approach has been to identify the range of design points as "max flow at min pressure" and "min flow at high pressure". I'm then following the Emerson/Fisher control valve handbook (4th edition) to calculate a Cv and choose a valve for each case. Then to get an idea of the useful range of each valve I've looked at the Cv for the valve chosen at 20%, 50% and 80% open.
The two valves I've ended up with seem to be able to do the job, the smaller 20%-80% Cvs being 0.15-0.83, the larger 0.85-7.07. Both are equal percentage characteristic. I'm a bit worried that there might not be enough overlap here.
Being a bit of a rookie at this I'm mainly looking for feedback on the method used, and any issues to hold in mind when specifying a dual valve system like this. Some of the "unknown unknowns" that a newbie like me might run into.
Thanks for any advice.
I have a case where a valve is needed for regulating the pressure inside a process. The issue is that the pressure setpoint(and flow required to maintain this pressure) varies quite a lot. The valve(s) is installed downstream of the process, and the process itself has inlet flow controlled.
The minimum flow is on the order of 10% of design flow, max flow 120% of design. Pressure setpoint can vary anywhere between 3 barg to 8 barg (but not likely high pressure at low flows).
So far my approach has been to identify the range of design points as "max flow at min pressure" and "min flow at high pressure". I'm then following the Emerson/Fisher control valve handbook (4th edition) to calculate a Cv and choose a valve for each case. Then to get an idea of the useful range of each valve I've looked at the Cv for the valve chosen at 20%, 50% and 80% open.
The two valves I've ended up with seem to be able to do the job, the smaller 20%-80% Cvs being 0.15-0.83, the larger 0.85-7.07. Both are equal percentage characteristic. I'm a bit worried that there might not be enough overlap here.
Being a bit of a rookie at this I'm mainly looking for feedback on the method used, and any issues to hold in mind when specifying a dual valve system like this. Some of the "unknown unknowns" that a newbie like me might run into.
Thanks for any advice.