Oremus
Mechanical
- Jan 22, 2008
- 85
I'm designing a sprinkler system for a little 7,000 sq. ft. warehouse with about 1/4 of it being group 'b' occupancy and the actual warehouse being S-1 occupancy. This is split down the middle to accommodate two tenants. The fire sprinkler contractor estimated this project based upon ordinary group II water densities but I don't think that's appropriate given the speculative nature of who and what might go in these spaces. This is a simple metal warehouse building and the highest point is at about 25 ft. I would say max storage you could possibly stack to would be about 20 ft. I'm thinking if they don't have a specific occupant or are not going to limit what is stored and how high then this should probably fall under the city's 'speculative warehouse' ruling which requires a .64 gpm / 2000 sq. ft. density which totally blows away their bid price and may even require a fire pump. Am I going overboard or should we just stick to the ordinary group II and state on plans and to owner that this only allows storage to 12 ft of up to class IV commodity with no group 'A' plastics etc...
Does anyone have any advice on how to approach this?
THanks,
Oremus
Does anyone have any advice on how to approach this?