Split core ct use in a power transformer

Status
Not open for further replies.

apowerengr

Electrical
Jul 19, 2006
208
Does anyone have experience with FAGET TM2000 CT's? I have a power transformer supplier quoting these CT's in a proposed unit - 70MVA 138kV-26.4kV delta-wye gnd. I'm somewhat concerned with using split-core CT's in a power transformer for protection.

Any feedback on these ct's or on the use of split-core ct's in a power transformer would be appreciated.
 
Replies continue below

Recommended for you

Where are the CTs being installed? I think the type CT you reference is for installation on <600V bus bar.

When you say "CTs used in power transformer" I tend to think of CTs installed about the transformer bushings (normally under oil in a transformer).

 