Dear eng-tips members
The 14 tons of hot water supply enter to the reboiler and
return through two valves in parallel,and the pipe size is 8" the hot water return header.
And, the split range control is used here to control flow
in a broad range.
Our leader suggest that the low range valve is changed from 8" to 6"and high range valve is set to be 8".
He said that the low range valve should be smaller size than high range valve size.
But the flow meter FT located on the upstream 8" pipe is common to both valves. so is it necessary to change to low range valve size to be smaller 6"?
And, usually the smaller valve is sized to 1/3 of the system capacity, and large valve is twice as big so is that means I
have to size the smaller valve based on the 1/3 flow capacity?
Thank you very much.