Hi all, I am a structural engineer in the process of renovating the kitchen in my personal residence. The configuration of the new kitchen conflicts with two of the existing pendant sprinkler heads so I indicated in the drawings that two sprinkler heads in the kitchen/dining area be relocated (within the kitchen and dining areas themselves). I recently submitted drawings to obtain a building permit and got some comments back from the mechanical/fire protection reviewer reviewer:
Sprinkler required in washer/dryer closet. Per NFPA 1 Section 13.3.2.16.2 "Closets that contain equipment such as washers, dryers, furnaces or water heaters shall be sprinklered regardless of size."
It turns out my unit has a small closet with the washer and dryer. The closet is away from the kitchen area and totally outside the area included in the scope of work. My question is whether the relocation of the two sprinkler heads in the kitchen triggers a requirement to sprinkle the small washer/dryer closet?
I noted that there is a pendant sprinkler head right outside the louvered wood bi-fold doors in the closet. If a sprinkler is indeed required in the closet, would this existing head count? I dont think there is even room inside the closet for a sprinkler since the dryer is stacked on top of the washer and its top is very close to the ceiling.
Thank you in advance for your feedback!
Sprinkler required in washer/dryer closet. Per NFPA 1 Section 13.3.2.16.2 "Closets that contain equipment such as washers, dryers, furnaces or water heaters shall be sprinklered regardless of size."
It turns out my unit has a small closet with the washer and dryer. The closet is away from the kitchen area and totally outside the area included in the scope of work. My question is whether the relocation of the two sprinkler heads in the kitchen triggers a requirement to sprinkle the small washer/dryer closet?
I noted that there is a pendant sprinkler head right outside the louvered wood bi-fold doors in the closet. If a sprinkler is indeed required in the closet, would this existing head count? I dont think there is even room inside the closet for a sprinkler since the dryer is stacked on top of the washer and its top is very close to the ceiling.
Thank you in advance for your feedback!