PrakMS
Mechanical
- Dec 5, 2013
- 8
Hi Guys,
I have the following situation in one of the projects i'm managing.
(Sorry for the length of the post, just thought that sometimes the question gets mis-interpreted if enough data is not provided)
The background goes like this, we are constructing a warehouse in 2200 Sq.m area with no internal compartmentalization. The warehouse height is 7.2 m and the building is having a roof truss arrangement. The storage racks for a height of 6 meters (3 levels) and the aisle width is 3.2 meters. The material inside is rubber, gloves, packing materials and non-flammable chemicals. We had hired a fire consultant to design the system as per NFPA, now the consultant has given his output and i'm having lot of clarifications in that output.
The consultant's outputs are as follows:
200 nos of Upright sprinklers with K-factor 115 for entire warehouse (to sprinkle the ceiling structural members)
200 nos of Pendant sprinklers with K-factor 115 for the entire building
1704 nos of In-rack sprinklers (one sprinkler head for each pallet unit) (including the top level)
3 nos of fire hoses or hose reel drums inside the building at various points
8 nos of stand posts /external hydrant posts around the warehouse
Underground water tank of capacity 350 KL with 2 pumps of 273 CMH (1 diesel + 1 electric) and 1 jockey of 10.8 CMH
My clarification is very simple, whether you need a sprinkler head for each pallet unit and also how to calculate the water demand for the entire fire protection system (including sprinklers+fire hoses+stand posts which i have mentioned)
It would be of great help if you guys can clear this up.
Thanks in Advance....
I have the following situation in one of the projects i'm managing.
(Sorry for the length of the post, just thought that sometimes the question gets mis-interpreted if enough data is not provided)
The background goes like this, we are constructing a warehouse in 2200 Sq.m area with no internal compartmentalization. The warehouse height is 7.2 m and the building is having a roof truss arrangement. The storage racks for a height of 6 meters (3 levels) and the aisle width is 3.2 meters. The material inside is rubber, gloves, packing materials and non-flammable chemicals. We had hired a fire consultant to design the system as per NFPA, now the consultant has given his output and i'm having lot of clarifications in that output.
The consultant's outputs are as follows:
200 nos of Upright sprinklers with K-factor 115 for entire warehouse (to sprinkle the ceiling structural members)
200 nos of Pendant sprinklers with K-factor 115 for the entire building
1704 nos of In-rack sprinklers (one sprinkler head for each pallet unit) (including the top level)
3 nos of fire hoses or hose reel drums inside the building at various points
8 nos of stand posts /external hydrant posts around the warehouse
Underground water tank of capacity 350 KL with 2 pumps of 273 CMH (1 diesel + 1 electric) and 1 jockey of 10.8 CMH
My clarification is very simple, whether you need a sprinkler head for each pallet unit and also how to calculate the water demand for the entire fire protection system (including sprinklers+fire hoses+stand posts which i have mentioned)
It would be of great help if you guys can clear this up.
Thanks in Advance....