acb324
Mechanical
- Aug 15, 2012
- 39
When are sprinklers required under an overhang on a building per NFPA 13? My confusion is caused by the annex in this instance.
NFPA 13 (2010) 8.15.7.2 states that sprinklers can be omitted from beneath projections that are non-combustible. Period. Nothing about the occupancy above the overhang is mentioned.
However, the corresponding annex material A8.15.7.2 states that areas under exterior ceilings where the building is sprinklered should be protected due to the occupancy above. Is there a reference in the actual document (as opposed to the annex) that bolsters this? Each time I provide sprinkler coverage under these circumstances I am asked to defend it and would like to know if there is something better than the annex to support it.
I have a building that looks like an inverted tiered cake, with the second floor larger than the first, causing an exterior overhang exceeding 4'. In my opinion this should have sprinkler coverage due to the sprinklered occupancy above. Can anyone clarify?
NFPA 13 (2010) 8.15.7.2 states that sprinklers can be omitted from beneath projections that are non-combustible. Period. Nothing about the occupancy above the overhang is mentioned.
However, the corresponding annex material A8.15.7.2 states that areas under exterior ceilings where the building is sprinklered should be protected due to the occupancy above. Is there a reference in the actual document (as opposed to the annex) that bolsters this? Each time I provide sprinkler coverage under these circumstances I am asked to defend it and would like to know if there is something better than the annex to support it.
I have a building that looks like an inverted tiered cake, with the second floor larger than the first, causing an exterior overhang exceeding 4'. In my opinion this should have sprinkler coverage due to the sprinklered occupancy above. Can anyone clarify?