Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

SRV Question

Status
Not open for further replies.

brandonb73

Mechanical
Feb 22, 2008
54
On a Section I boiler, the manufacturer provided a 3" FNPT connection for the SRV, but the SRV that was provided has a 2" MNPT connection.

Question #1: It is my interpret PG-71.3 that the connection between the boiler and the SRV must be the same size as the SRV inlet (2"), not necessarily the boiler connection, meaning it can be reduced. Is this correct?

Question #2: Am I permitted to install a threaded flange set on the inlet of the valve to make removal of the valve easier? PG-71.2 prohibits any "unnecessary" pipe or fittings in the area. Is a flange considered unnecessary?

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor